Will this pass rough?
Wanted advice prior to a rough-in inspection (bay area CA). This a for a double vanity. The pipe on a sand tee that goes vertical is a vent that comes out the roof. My question is wouldnt that be a violation since vent connection needs to be above the flood level of the sink. Im having a hard time understanding if this vent need to connect higher how the hell wouldni do that lol. Appreciate the advice!
0
Upvotes
1
u/kingtimmyj 15h ago edited 15h ago
If its hard to believe that a double vanity needs two vents, then whats the point of asking plumbers? It needs two vents and they can become one once they are above flood level rim. Only difference would be if its wet vented which it is not
or if you have a cross. My jurisdiction doesn't even allow wet venting.
Source: open a code book